I was installing a Generac Generator the other day with a 12 space automatic transfer panel. While choosing the 12 circuits that would be attached to the transfer panel, I realized that if the existing house wiring has 2 circuits tied together at some point (we've never seen an unintentional joining of 2 circuits before) and one circuit was in the transfer panel and the other not, then this would bypass the effect of the transfer switch and place voltage back on the main bus and the power lines.
I know we cannot be responsible for others mistakes, but this seemed pretty scary. Any thoughts? Has this happened? I thought to test for voltage at the main bus with the generator on, but this would not cover connections thru switches.
Thanks,
Mark
I know we cannot be responsible for others mistakes, but this seemed pretty scary. Any thoughts? Has this happened? I thought to test for voltage at the main bus with the generator on, but this would not cover connections thru switches.
Thanks,