Hi experts,
I am calculating the SCCR value and improving the rating but am not sure whether it is right or wrong.
I only need to meet the requirements for NEC and NFPA70/79, excluding UL508A.
However, NFPA and NEC require the calculation and marking of the panel SCCR.
The SCCR requirement from our facility is 65KA@480V
1. We have three 24VDC power suppliers supplied directly from the main branch at 480V.
I know there is no requirement for the 24VDC power supplier and its load.
How about the feeding breaker for these supplies?
For each 24VDC power supply, I am using a UL489 MCB with a breaking capacity of 10KA at 480V.
Will these three breakers affect the panel SCCR rating, or do I need to add a CC class fuse to enhance this branch's SCCR?
2. There is a cooling unit for the panel marked with a 5KA SCCR, powered from the 480V main branch without TR.
Do I need to add a CC class fuse to enhance the whole panel's SCCR rating?
3. There is a remote hydraulic system with a pump motor connected via an aviation plug,
and the aviation plug has no data about SCCR.
Do I need to add a CC class fuse to enhance the whole panel's SCCR rating?
4. For the SCCR rating calculation and label, is that a must to use UL listed components?
For example , The main breaker(infeed) for this panel is not a UL listed breaker,
and it doesn't mention the SCCR rating or interrupt rating by UL standard.
Could I just use the Ics value from maker for the SCCR calculation for this panel?
I am confusing for this part because the SCCR rating seems is not always as same as the Ics by maker's data.
Thank you!
I am calculating the SCCR value and improving the rating but am not sure whether it is right or wrong.
I only need to meet the requirements for NEC and NFPA70/79, excluding UL508A.
However, NFPA and NEC require the calculation and marking of the panel SCCR.
The SCCR requirement from our facility is 65KA@480V
1. We have three 24VDC power suppliers supplied directly from the main branch at 480V.
I know there is no requirement for the 24VDC power supplier and its load.
How about the feeding breaker for these supplies?
For each 24VDC power supply, I am using a UL489 MCB with a breaking capacity of 10KA at 480V.
Will these three breakers affect the panel SCCR rating, or do I need to add a CC class fuse to enhance this branch's SCCR?
2. There is a cooling unit for the panel marked with a 5KA SCCR, powered from the 480V main branch without TR.
Do I need to add a CC class fuse to enhance the whole panel's SCCR rating?
3. There is a remote hydraulic system with a pump motor connected via an aviation plug,
and the aviation plug has no data about SCCR.
Do I need to add a CC class fuse to enhance the whole panel's SCCR rating?
4. For the SCCR rating calculation and label, is that a must to use UL listed components?
For example , The main breaker(infeed) for this panel is not a UL listed breaker,
and it doesn't mention the SCCR rating or interrupt rating by UL standard.
Could I just use the Ics value from maker for the SCCR calculation for this panel?
I am confusing for this part because the SCCR rating seems is not always as same as the Ics by maker's data.
Thank you!