You could tell them to build the control panel to have a 75KA SCCR and be covered no mater what, but that could add a lot to the cost that may not be needed. Since you are using RK1 fuses in the buss disconnect and all of your busses are less then 100KA, you could reduce the SCCR down based upon the size of the fuse you put into the disconnect. I would assume the fusing is based on the individual piece of equipment, so it would always be fused the same without regards to the buss it is connected to. For example, If you have a piece of equipment that requires 200A branch circuit protection and you use a LPS-RK-200SP, Per UL508A, table SB4.2, the panel would only need a SCCR of 22KA