I'm going to use a solid-state relay for controlling a 208V single-phase heater by turning it on/off. Basically, it's a transistor contactor. The power will come off of a main three-pole breaker, to a bus, then from the bus to a two-pole breaker, one leg of the breaker will go through the SSR to the heater and the other leg will go directly to the heater (see attached)
When I had done a three phase heater design in the past, the three phase SSR had a SCCR value listed in its spec sheet. The SSR that my manager want to go with for this project, an RSCDN-30A from IDEC, didn't list an SCCR value. When I contacted IDEC, they informed me that it did not need an SCCR value because it's part of the control circuit, not the power circuit. Am I wrong thinking that this 30A SSR should be part of the power circuit?
When I had done a three phase heater design in the past, the three phase SSR had a SCCR value listed in its spec sheet. The SSR that my manager want to go with for this project, an RSCDN-30A from IDEC, didn't list an SCCR value. When I contacted IDEC, they informed me that it did not need an SCCR value because it's part of the control circuit, not the power circuit. Am I wrong thinking that this 30A SSR should be part of the power circuit?