Davebones
Senior Member
- Location
- North Of Tampa Fl
Had some equipment come in with 5ka sccr rating . It will be fed from a bus with available fault current of 30,000 amps . We will be feeding the machine with a 100 amp bus switch fused at 100 amps . The 100 amp fuses ( LLSRK-Id ) fuses show let-thru current as 4,100 amps . Is this correct for meeting the 5KA sccr rating of the machine ?