I have a job coming up where the 3/4" Sch 40 PVC is underground. Where it emerges above grade I will be moving over to Sch 80 for about 12". My dilemma, the conduit fill is fine for the Sch 40 but for the Sch 80 is "over filled" by .0092
Do I need to rethink the conduit size needed for the entire run or let it "ride"?
I can live with .0092 myself because I've been in this exact situation before. The next time it comes up I'll use larger conduit.
I'm pulling 3 #6 and 1 #10 for a panel in a Garage. I will be driving ground rod(s) at the Garage.
My solutions:
1. Reduced neutral, use #8. Surely they'll have some 240v load out there. AC/Air Compressor/Heaters/Welder, etc.
2. Pull in a bare #10 and squeek under the fill requirements.
3. Leave it the way it is. If the inspector bocks at it, explain what happened and tell him you'll know to use larger conduit next time. If he still bocks at it, pull the wire out just far enough to just strip the insulation off the ground wire where it passes through the sch. 80 and then reinstall.
Do I get credit for thinking outside the box?