How is schedule 80 P.V.C equivalent to rigid conduit? Does anyone know the technical data?
Thanks
JJ
Thanks
JJ
JJWalecka said:I was under the understanding that PVC schedule 80 can be used in substitution to rigid under certain applications. Was I mislead?
The marking ??Schedule 80 PVC?? identifies conduit suitable for use whereexposed to physical damage and for installation on poles in accordance with the NEC.
JJWalecka said:I never understood that it was the equal… especially in the cold!
Its not equivalent. PVC is a great choice for some things, and rigid is a good choice for others.JJWalecka said:How is schedule 80 P.V.C equivalent to rigid conduit? Does anyone know the technical data?
Since Schedule 40 has 1/4" wall and Schedule 80 has 3/8" wall, it is only 1 1/2 times . . .cowboyjwc said:. . . not one person said "schedule 80 is twice as good as schedule 40."
Can't use pvc for receptacles in health care 517.13(B) requires equipment grounding conductor to be insulated copper and installed in metal raceways or part of a listed cable having a metallic armor or sheath.Ragin Cajun said:Well for one thing, compared to RGC, Sched 80 ain't a conductor! ;-) so you can't use it or any PVC where you need the conduit to serve as the EGC or as a redundant EGC such as in medical facilities. I guess you could pull two EGC's in PVC???
RC
cowboyjwc said:Also neither schedule 40 or 80 are mentioned in the NEC that I know of, all it mentions is Rigid Nonmetallic Conduit.
Rigid non metallic conduit is no longer in the 08 NEC. Its now PVC Sch 40 or 80JJWalecka said:I was under the understanding that PVC schedule 80 can be used in substitution to rigid under certain applications. Was I mislead?
"Also neither schedule 40 or 80 are mentioned in the NEC that I know of, all it mentions is Rigid Nonmetallic Conduit." Never thought of that.
JJ