lmchenry said:
Do you know of any code NEC or otherwise that pertains to PVC run in schools?
Kinda yes, kinda no. . Depends on what part of the school building you're talking about.
Article518 for 100 occupancy or more
518.4(A) says nonmet raceways must be encased in 2" of concrete.
But 518.2(B) says: "Article 518 applies only to that portion of the building considered an assembly occupancy." . So it depends on what room you're talking about.
For a theater in a school of
any occupancy size, 518.2(C) says look at 520. . And 520.5(A) says nonmet raceways must be encased in 2" of concrete.
lmchenry said:
I have had someone tell me that pvc is not allowed in schools above grade.
"above grade"
kinda, it's not abovegrade/belowgrade, it's actually inside/outside
230.6 says under the slab is outside of the building.
Altho 230 is services, that concept is used for any application.