We have a scoreboard mounted 12' above ground outdoors. There are individual units each powered by a 120v receptacles. Is there any reason those receptacles would not be required to be GFCI based on 210.8(B)(4) ?
Read 210.8(B) and show us where the term "from the ground" is used.Since the reasoning for having GFCI protected receptacles in a residential garage, is to protect someone plugging in an extension cord, and going outside with it. The NEC says if accessible from the ground. Is the scoreboard accessible from the ground ?
Of course they're not the same, not to mention the file you posted is simply someones opinion, not code words. If you are going to quote something to substantiate your stance it needs to be a current NECSee Article 100 - Definitions Accessible, Readily (Readily Accessible).
This is an older 1999 NEC code, and code sections might not be the same for newer codes.
I think the requirement for GFCI protection is only for portable/mobile signs and must be provided by the manufacturer.Those receptacles are outside and require GFCI protection, but it would be my opinion that the parent text in 210.8 would prohibit the receptacles themselves from providing the required GFCI protection.
1999 NEC did not have nearly as many GFCI requirements for non dwelling applications as more recent editions do. From recollection mostly just rooftop receptacles and temporary power applications were most of what was needing GFCI for outdoors back then. 2005 and every edition after kept adding more to the requirements though.See Article 100 - Definitions Accessible, Readily (Readily Accessible).
This is an older 1999 NEC code, and code sections might not be the same for newer codes.
210.8(B)(3) OutdoorsI think the requirement for GFCI protection is only for portable/mobile signs and must be provided by the manufacturer.
I am not aware of any area that is still using the 1993 code.NEC 1993, Section 210-8(3) "For the purpose of this section, "direct grade level access" is defined as being located not more than 6 feet, 6 inches (1.98 m) above grade level and beng readily accessible. I believe that's where I got it in my head as requiring it to be accessible from the ground level.
I am not aware of any area that is still using the 1993 code.
The parent text in 210.8 has required that the GFCI device be installed in a readily accessible location since the 2011 code.
We have a scoreboard mounted 12' above ground outdoors. There are individual units each powered by a 120v receptacles. Is there any reason those receptacles would not be required to be GFCI based on 210.8(B)(4) ?
The receptacle does not have to be readily accessible, only the GFCI device that protects the receptacle has to be readily accessible.Is 12 feet above ground "Readily Accessible" ?
210.8(B)(3) Outdoors