If I could make a suggestion based on experience …..
GFCI protect them either at the breaker, or ideally from a device in a protected location nearby the scoreboard to limit the load-side circuit length on the GFCI.
I coached a little-league team for a few seasons. Before one of our games, i was walking by the scoreboard and noticed the PVC conduit running up the pole had been hit by a mower, and they took the UF inside and wrapped it around the outfield fence; the end of the cable was stripped bare for several inches from the mower blade cutting it. I got my meter from the truck and tested from the fence to the EGC in the UF, and there was 120v on the fence. The panel was located inside a maintenance shed and locked. I found the site director to get access to turn it off. When I asked if he was aware of the wire, he stated that he was aware, and had simply forgotten to have someone come fix it. I do wonder if maybe the breaker tripped, and someone else reset the breaker trying to get the scoreboard on that morning being unaware that the wire had been damaged.
I built a large 8-field baseball complex back in 2020, and with that experience in mind, we installed dead-front GFCI’s in the scorekeepers booth behind home plate and ran the conduit straight out to the scoreboard, transitioning to GRC underground and up the pole. We had receptacles in the dugouts as well, and I used GRC and cast boxes on everything.
Sent from my iPhone using Tapatalk