Realized today that some of our electric furnaces use Scott transformers to provide two separate single phase voltages to two separate heating element banks (ungrounded) from our 480 3-phase power. Was wondering a couple things. First, if you connected one leg of each of the two single phases to ground, what would be ratio from hot/hot to hot/neutral? 1.414 to 1.0? Second, when two phase power is used for two phase motors, what if anything is grounded?
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
There are a bunch of different flavors of two phase power; 3, 4, and 5 wire to name a few. It sounds like you have '4 wire' with two wires for each of 2 phases.

If you joined one leg from each of the 2 phases you would end up with '3 wire'; the hot-hot : hot-common ratio is 1.414:1.0 as you surmised.

Note that the 'common' wire is not 'neutral' and it doesn't need to be grounded. But the common would be the grounded conductor _if_ a conductor were grounded.

'5' wire has two center tapped phases. The center taps are joined as common. This gives you two choices for hot-hot, same phase or different phase. The hot-hot: hot-common ratio is either 2.0:1.0 or 1.414:1.0

If the 5 wire system is grounded, then the common is the grounded conductor.

-Jon
 