Saturn_Europa
- Fishing Industry
- Electrician Limited License NC
I have a 35 Kw, NEMA 3R, 480 Y to 208 Y transformer at my plant. X0 has a bonding jumper attached to the ground lug on the case of the transformer, the grounding electrode conductor is also attached to a ground lug on the case of the transformer then to some building steel. Five feet from the transformer is the 208 panel board. It has a system bonding jumper connected to the neutral bus bar. There is also a EGC from the panel board to the case of the transformer.
My question is: Doesnt this set up a parallel path to the source? Should I lift the system bonding jumper at the panel board?