Re: SDS Grounding
Scott,
I see nothing in the NEC that says a SDS must be in the same building or structure as the primary. In my opinion, transformers on a campus or industrial distribution system that are not utility owned are SDS.
Any transformer that is on the load side of the service point is covered by the NEC and is a SDS.
Don
Scott,
I see nothing in the NEC that says a SDS must be in the same building or structure as the primary. In my opinion, transformers on a campus or industrial distribution system that are not utility owned are SDS.
Any transformer that is on the load side of the service point is covered by the NEC and is a SDS.
Don