rojay
Senior Member
- Location
- Chicago,IL USA
I’m reviewing a set of plans for a new generator install. Gennie is 3 phase 277/480 with a 1000 amp feeder breaker. The feeder supplies a 480 volt generator distribution switchboard where emergency & optional standby loads are split off to step down transformers (emergency & optional standby loads are 120/208 volt) before hitting their separate transfer switches. The optional standby transfer switch is solid neutral & contains the service disconnect. Questions- how can the generator be considered a non separately derived system and rely on the building service grounding when there’s a transformer between it and the transfer switch? Shouldn’t the neutral be bonded at the genset & connected to a separate grounding electrode system? If the generator is solidly grounded isn’t a ground fault signaling device required too?