jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
You could read it that way. But is the bond at the service really on the 'load side' of the transfer switch? It's sort of off to the side.The EM transformer secondary conductors terminate at the transfer switch. Without an overcurrent device at the EM transfer switch (unlike the OSS transfer switch) aren’t I stuck having to add the SBJ at the EM transformer and do my grounding there?
I don't think the code section was written with this situation in mind.
I agree that the code requirements are clearer if you switch the neutral.