Four SDS senerios:
All four senerios have 4 - 600 Kcmil conductors in 4 raceways between transformer enclosure and the OCPD is some 30 feet away.
Transformer is outside and the OCPD is in an adjacent building.
1) Bonding Jumper ( BJ ) 250.30(A)(1) is at the transformer Xo location. The 4 raceways have a metal (RMC) 90? at each end of a RNC run.
2) BJ is at the OCPD. The 4 raceways have a metal (RMC) 90? at each end of a RNC run.
3) BJ is at the transformer Xo location. The four runs of conduit are all RMC.
4) BJ is at the OCPD location. The four conduit runs are all RMC.
Question(s),
What size conduit bonding conductor and how to accomplish the proper grounding of the metal portions of the raceways in each senerio above ?
Use 2002 NEC substantations.
All four senerios have 4 - 600 Kcmil conductors in 4 raceways between transformer enclosure and the OCPD is some 30 feet away.
Transformer is outside and the OCPD is in an adjacent building.
1) Bonding Jumper ( BJ ) 250.30(A)(1) is at the transformer Xo location. The 4 raceways have a metal (RMC) 90? at each end of a RNC run.
2) BJ is at the OCPD. The 4 raceways have a metal (RMC) 90? at each end of a RNC run.
3) BJ is at the transformer Xo location. The four runs of conduit are all RMC.
4) BJ is at the OCPD location. The four conduit runs are all RMC.
Question(s),
What size conduit bonding conductor and how to accomplish the proper grounding of the metal portions of the raceways in each senerio above ?
Use 2002 NEC substantations.