Andy1099
Member
- Location
- jackson wy USA
I was recently failed on a project. I could not come into the back of an enclosure mounted on the outside of a house so I penetrated the wall just below the enclosure and ran SE cable into the bottom of the enclosure. I build a soffit around the SE cable to protect from physical damage. The inspector failed me, and after reading the code I cannot see that he is wrong. Yet, I want to verify. The inspector says that per 338.10(B)(4)(3)(b)(1) when installed outside, I need to comply with part one of article 225. Article 225.20 says conductors installed on building structures or poles shall be protected against physical damage as provided in 230.50. Article 230.50 says they need to be installed in conduit. What am I missing?