Re: SE Cable
Iwire,
You stated.....
"As for the load end just ask for a lug rated 75C or one that can take a 1/0 but is still listed for 6 awg as used in the example."
The 1999 NEC 110-14(c)(3) says you cannot just buy a lug and install it on a device that is rated 60C to increase the effective terminal temperature rating.. At least that is how I read it.
I have talked to Square D and they were not able to confirm to me that their QO or hom,eline breakers were rated 75C. They were supposed to send me technical info, but I never got it. If you can direct me to technical info that depicts 0-100 amp load center or panelboard plug on breakers rated 75C I would very much like to see it.
mweaver
Iwire,
You stated.....
"As for the load end just ask for a lug rated 75C or one that can take a 1/0 but is still listed for 6 awg as used in the example."
The 1999 NEC 110-14(c)(3) says you cannot just buy a lug and install it on a device that is rated 60C to increase the effective terminal temperature rating.. At least that is how I read it.
I have talked to Square D and they were not able to confirm to me that their QO or hom,eline breakers were rated 75C. They were supposed to send me technical info, but I never got it. If you can direct me to technical info that depicts 0-100 amp load center or panelboard plug on breakers rated 75C I would very much like to see it.