SE-R cable

Status
Not open for further replies.

sparky76

Senior Member
Location
So Cal
Cant find my code book. What is the max amp rating for 2-2-2-4 AL, SE-R cable when the conductors are XHHW-2? It will be used as a subfeed in a residence. Thanks in advance.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Are you using the 2008 NEC as the answer depends on what code cycle you are working under.

Under the 2005 NEC using Table 310.16 and the 75 degree column #2 Aluminum SER cable has an ampacity of 90 amps.

Under the 2008 NEC due to a change in 338.10(B)(4)(a) you are limited to the 60 degree column of Table 310.16 so the ampacity of #2 Aluminum SER cable is 75 amps.

I am assuming by the use of the term "subfeeding" the that feeder in question is not a main power feeder and Table 310.15(B)(6) would not apply.

Chris
 

jwjrw

Senior Member
Everyone here is just down sizing to a 150 amp service and using 4/0 instead of going to 250mcm
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Everyone here is just down sizing to a 150 amp service and using 4/0 instead of going to 250mcm

Under the 2008 NEC 250 Kcmil Aluminum SER cable has an ampacity of 170 amps at 60 degrees C. Using 240.4(B) you can only go up to a 175 amp breaker. Again this is for feeders that don't qualify as a main power feeder for a dwelling unit.

Chris
 

jwjrw

Senior Member
Under the 2008 NEC 250 Kcmil Aluminum SER cable has an ampacity of 170 amps at 60 degrees C. Using 240.4(B) you can only go up to a 175 amp breaker. Again this is for feeders that don't qualify as a main power feeder for a dwelling unit.

Chris

You are right. I was stating what other people are doing in the area by usine 4/0 and a 150 amp. The parts house had the change in se cable there last year and I overheard 250. I should of checked before I posted sorry.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
You are right. I was stating what other people are doing in the area by usine 4/0 and a 150 amp. The parts house had the change in se cable there last year and I overheard 250. I should of checked before I posted sorry.

Not a problem.:)

I have just had heard some places had felt that 250 Kcmil SER cable was was Ok for a 200 amp feeder under the 2008 NEC by using 240.4(B). They just forgot that 240.6 lists a 175 amp breaker.;):)

The 4/0 with a 150 amp breaker is the best solution that I have seen as well.

Chris
 

Jerseydaze

Senior Member
OK I'm confused I want to run a 200 amp main breaker to a 200 amp sub panel residential what size wire xhhw do i need 2008 Nec
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
OK I'm confused I want to run a 200 amp main breaker to a 200 amp sub panel residential what size wire xhhw do i need 2008 Nec
Unfortunately, under the 2008 Code that has become an AHJ call.
Depending on how the authority looks at 310.15(B)(6), 215.2 and 338.10(B)(4), a 4/0 SER on an interior installation might be considered a 200 amp cable, or a 150 amp cable.
 