Since 90 amps is listed as a standard size for a breaker in 240.6, I believe that you can not upsize to a 100 amp breaker.
Everyone here is just down sizing to a 150 amp service and using 4/0 instead of going to 250mcm
Under the 2008 NEC 250 Kcmil Aluminum SER cable has an ampacity of 170 amps at 60 degrees C. Using 240.4(B) you can only go up to a 175 amp breaker. Again this is for feeders that don't qualify as a main power feeder for a dwelling unit.
Chris
Everyone here is just down sizing to a 150 amp service and using 4/0 instead of going to 250mcm
Is that in lieu of SE 4/0 200A Main?
You are right. I was stating what other people are doing in the area by usine 4/0 and a 150 amp. The parts house had the change in se cable there last year and I overheard 250. I should of checked before I posted sorry.
Unfortunately, under the 2008 Code that has become an AHJ call.OK I'm confused I want to run a 200 amp main breaker to a 200 amp sub panel residential what size wire xhhw do i need 2008 Nec
OK I'm confused I want to run a 200 amp main breaker to a 200 amp sub panel residential what size wire xhhw do i need 2008 Nec
If its individual conductors 4/0 xhhw copper 2/0, alum 4/0
If its ser thats 300mcm I believe