What is the approved way of maintaining the enclosure NEMA rating with PVC conduit? Answer yes or no, for the following.
PVC Male adapter with sealing locknut on the interior
PVC Male adapter with O-ring gasket on the exterior and standard locknut on the interior
PVC Male adapter with Myers hub
PVC Male adapter wtih sealing locknut on exterior (gasket facing enclosure), and standard locknut on interior
I think yes to all (assuming the o-ring gasket is part of a listed fitting).
However, the real answer comes from UL who tells you what you must do to maintain the type rating of an enclosure. there is a series of charts in UL508a that shows what means of sealing holes works with what type of enclosures and what the type rating is of the result.