Can non metallica sealtight be usec from meter pan to panel Cleaning up a horrible install Sealtight will give me the tight flexibiity
The list in 230.43 is quite long (19 in the 2017) and does allow non-metallic seal tight.There is a list in the NEC for the allowed type of wiring methods for service entrance conductors. The wiring methods are restricted for unfused conductors.
Compared to the NEC that is very restrictive.Some utilities also have rules about the wiring method between the meter and the service equipment.
Our local code only permits RMC or IMC for service conductors, with an exception for an underground service that permits PVC with an expansion fitting between the earth and the meter.
it is, but that has been our local code for a long time. It also specifies a maximum length of 10' from the point of entrance for service conductors.Compared to the NEC that is very restrictive.