I have big land in which there is going to be new Amphitheater.

Please see attached sketch has one line left side and site plan right side. One line shows the utility transformer secondary has a set of service conductor to existing panel which then feeds irrigation pump only. The site plan shows existing panel is located 14 feet from the utility transformer.

The utility transformer secondary attached sketch one line shows also has additional new sets of service conductors which is going to feed the new Amphitheater. The site plan shows Amphitheater is located 450 feet from the utility transformer.

I searched in NEC 2014 but did Not find any exception that would allow for the new service conductor to feed Amphitheater or cannot find any exception for irrigation pump to have its existing separate service but I am not sure if I am correct or incorrect.

I just want to verify does NEC 2014 allow new second service or irrigation pump allowed have its own service or altogether the irrigation pump and Amphitheater need to be on one service fed from one utility transformer or Amphitheater can be fed from new utility transformer and keep the existing utility transformer to feed for irrigation only?

a20688ead6d0c54ce10a83be78b8452c.jpg
 
Sure, It's two different sites 45-' away. No different from POCO supply two,three, four houses from 1 transformer.
 