I'm stuck with a 480 3 phase 40 amp site line that I'm hooking up to some containers that have a a/c spec at 208-230V 15A. 2 amps of 120 lighting the occasional 20 amp 220 welder and some intermittent power tools so peak current is likely something around the 35a 220 and 20a 120 loss with nominal around 7A 220 only. I'd like someone to double check my asssumptions here and let me know if I'm missing something.
I'm considering a 20kva 3 phase delta primary to 120/240 delta secondary dry transformer with impedance around 5%. The Wye type being out of phase gave a 208 output which given losses over the length of the line would go below the spec of the a/c. Is this the correct transformer type and size for these needs and are there any considerations I should keep in mind to this specific type of setup other that the hot/wild line ?
I'm considering a 20kva 3 phase delta primary to 120/240 delta secondary dry transformer with impedance around 5%. The Wye type being out of phase gave a 208 output which given losses over the length of the line would go below the spec of the a/c. Is this the correct transformer type and size for these needs and are there any considerations I should keep in mind to this specific type of setup other that the hot/wild line ?