I have spent the last few days reading a lot of the threads here on the forum concerning the sizing and protection of the secondary conductors of a transformer, and now I would like to compare what I think I know, to a transformer installation job we just had done that I am having issues with.
“We just had a 480/208Y/120V 45KVA transformer installed, and it is being supplied with a 60 amp circuit breaker from a distribution cabinet on the primary (3 wire) side wired with 8 AWG THHN, and coming off the secondary (4 wire) side we have AWG 2 THHN (ABC:N) and this is feeding a single 225 amp rated 30 pole panel not over 25 feet away with a 125 amp main.”
My concerns are these. I feel the wire on both the primary side and the secondary side are undersized.
When I work the math for the transformer I get: 45000 / (480x1.732) = 54.128 amps of primary current.
45000 / (208x1.732) = 124.911 amps of secondary current.
Looking at the 2008 NEC Handbook, Article 450 shows a nice picture of Primary Overcurrent Portection Only which is what the electrical contractor tried to setup, in my opinion.
When I work the math for the Primary Overcurrent Portection Only according to Table 450.3(B) I get: 54.128 amps x 1.25 = 67.660 amps as a maximum CB size. I don’t want to go above 125% and have to add secondary overcurrent protection so to stay with Primary Overcurrent Portection Only the CB size according to 240.6 is rolled back to 60 amp and according to Table 310.16 the size of the wire should be a 6 AWG THHN, @ 75 degrees C. So, in my opinion feeding this 45KVA transformer with a 60 amp CB on the primary side is fine, but the 8 AWG THHN should be removed, and replaced 6 AWG THHN. So, because there is Primary Overcurrent Portection Only, table 450.3(B) does not require the 45KVA transformer to have secondary overcurrent protection. But the secondary is feeding a single panel with a 125 amp main, so according to 240.4, 240.21(C) that wire needs to be sized based on the 125 amp main in the panel, which means the 8 AWG, THHN should be removed and replaced with size 1 AWG THHN, @ 75 degrees. All opinions are welcome.
Thanks,
Kevin
“We just had a 480/208Y/120V 45KVA transformer installed, and it is being supplied with a 60 amp circuit breaker from a distribution cabinet on the primary (3 wire) side wired with 8 AWG THHN, and coming off the secondary (4 wire) side we have AWG 2 THHN (ABC:N) and this is feeding a single 225 amp rated 30 pole panel not over 25 feet away with a 125 amp main.”
My concerns are these. I feel the wire on both the primary side and the secondary side are undersized.
When I work the math for the transformer I get: 45000 / (480x1.732) = 54.128 amps of primary current.
45000 / (208x1.732) = 124.911 amps of secondary current.
Looking at the 2008 NEC Handbook, Article 450 shows a nice picture of Primary Overcurrent Portection Only which is what the electrical contractor tried to setup, in my opinion.
When I work the math for the Primary Overcurrent Portection Only according to Table 450.3(B) I get: 54.128 amps x 1.25 = 67.660 amps as a maximum CB size. I don’t want to go above 125% and have to add secondary overcurrent protection so to stay with Primary Overcurrent Portection Only the CB size according to 240.6 is rolled back to 60 amp and according to Table 310.16 the size of the wire should be a 6 AWG THHN, @ 75 degrees C. So, in my opinion feeding this 45KVA transformer with a 60 amp CB on the primary side is fine, but the 8 AWG THHN should be removed, and replaced 6 AWG THHN. So, because there is Primary Overcurrent Portection Only, table 450.3(B) does not require the 45KVA transformer to have secondary overcurrent protection. But the secondary is feeding a single panel with a 125 amp main, so according to 240.4, 240.21(C) that wire needs to be sized based on the 125 amp main in the panel, which means the 8 AWG, THHN should be removed and replaced with size 1 AWG THHN, @ 75 degrees. All opinions are welcome.
Thanks,
Kevin