From an earlier post:
Heres my new project. I need to install a square D transformer (225 kva, 480 delta primary, 270 Primary side Amps, 208Y/120 Secondary, 625 Amp secondary) to power 3- 208/120, 200 Amp panels.
From what I understand from my other post, I may be able to run my cunductors directly from the secondary to the 200A panels with wire rated at 200A. Is this correct? 240.21 C(6) States that the secondary conductors shall have an ampacity that is not less than the value of the primary to secondary voltage ratio multipied by 1/3 of the rating of the OCPD protecting the primary of the transformer.
I don't understand the ratio section. I have a 480 primary and a 110V secondary.
So, that's 1:4 or 25%.
1/3 of the primary OCPD would be 350/3 or 117 A. 117 amps (25%) is 29 amps. This doesn't seem correct to me. Am I doing something wrong?
Connecting #10 wire to a transformer secondary with 626 Amps potential doesn't seem reasonabe!!
Thanks for your input.
Heres my new project. I need to install a square D transformer (225 kva, 480 delta primary, 270 Primary side Amps, 208Y/120 Secondary, 625 Amp secondary) to power 3- 208/120, 200 Amp panels.
From what I understand from my other post, I may be able to run my cunductors directly from the secondary to the 200A panels with wire rated at 200A. Is this correct? 240.21 C(6) States that the secondary conductors shall have an ampacity that is not less than the value of the primary to secondary voltage ratio multipied by 1/3 of the rating of the OCPD protecting the primary of the transformer.
I don't understand the ratio section. I have a 480 primary and a 110V secondary.
So, that's 1:4 or 25%.
1/3 of the primary OCPD would be 350/3 or 117 A. 117 amps (25%) is 29 amps. This doesn't seem correct to me. Am I doing something wrong?
Connecting #10 wire to a transformer secondary with 626 Amps potential doesn't seem reasonabe!!
Thanks for your input.