191017-1041 EDT
mbrooke:
Run an experiment.
Since there is no primary DC current, only secondary, you can use an electronic RMS current meter on the primary. Load the secondary with the sing;e diode, and raise the secondary load until the primary RMS current reaches the transformer rating. Do this at maximum expected primary voltage to pick the worst case.
After this determination you could do a transformer temperature rise measurement at this loading.
.
mbrooke:
Run an experiment.
Since there is no primary DC current, only secondary, you can use an electronic RMS current meter on the primary. Load the secondary with the sing;e diode, and raise the secondary load until the primary RMS current reaches the transformer rating. Do this at maximum expected primary voltage to pick the worst case.