wwhitney
- Berkeley, CA
- Retired
The section on Power Transformers in 705.30 has been changing every year, both in content and section letter. 705.30(C) indicates you mean the 2020 NEC, and it says in part "Secondary protection shall not be required for a transformer secondary that has a current rating not less than the sum of the rated continuous output currents of the power sources connected to that secondary."There is no OCPD required between the panels and the transformer as long as the total maximum output current of the inverters does not exceed the current rating of the transformer per 705.30(C).
But does that the secondary conductors or the secondary coil of the transformer itself? The 2023 NEC version makes it clear it meant the secondary coil itself. 705.30(F)(2) says "Transformer secondary conductors shall be protected in accordance with 240.21(C)."
So that's what the thread is about, how to comply with 240.21(C) when you have multiple non-parallel sets of secondary conductors, each sized to one or more of the inverters.
Cheers, Wayne