PhaseShift
I have a 25kVA 480-240/120 transformer. I am feeding the secondary of this transformer into an 100A 120/240V panel. The transformer and panel are located outdoors, and the panel will be about 10ft from transformer secondary. Per 240.21 (B) and (C) I planned on running a #2 from the secondary of the transformer to a 100A main breaker in the panel. Will this 100A breaker be adequate protection for the transformer secondary protection?
Also I will need to ground the transformer since it is a seperately derived system. I'm not sure what size GEC from table 250.66 to use for this application. I'm guessing that since my secondary condutors are #2 then I would use a #8 copper GEC from the neutral poing of the transformer to the grounding electrode.
What section specifies what size grounding electrode I need to use?
As far as sizing the neutral what section specifies the size neutral needed for this secondary? Will this neutral serve as the EGC between the transformer and panel as well?