Secondary overcurrent protection

Status
Not open for further replies.

shaw0486

Senior Member
Location
baltimore
On the secondary side of a 45 KVA delta wye transformed, you can use a fused disconnect if its within 10 feet but if you go over 10 feet you must use a enclosed circuit breaker. Can someone tell me if i am correct?
 
too many varibles for a blanket statement. You need to refer to 240.21(C)
 
On the secondary side of a 45 KVA delta wye transformed, you can use a fused disconnect if its within 10 feet but if you go over 10 feet you must use a enclosed circuit breaker. Can someone tell me if i am correct?
Protection for the transformer conductors can be either fuses or breakers at either distance.
 