Hello.
This is a new one for me. 600-480V three phase 45kVA autotransformer. It certainly requires primary overcurrent protection per 450.4. I believe it needs secondary overcurrent protection for the conductors, per article 240, but it's not clear reading through the Code. Also, it seems the 450.4 requirement for 125% protection of the primary side will limit the power on the secondary of this step down transformer.
Maybe it's simpler than I think and I can treat it like a standard delta-wye with overcurrent protection on primary and secondary side. Thoughts?
This is a new one for me. 600-480V three phase 45kVA autotransformer. It certainly requires primary overcurrent protection per 450.4. I believe it needs secondary overcurrent protection for the conductors, per article 240, but it's not clear reading through the Code. Also, it seems the 450.4 requirement for 125% protection of the primary side will limit the power on the secondary of this step down transformer.