This question is sort of along the lines of an existing post I have on secondary transformer protection however this one is focused on a utility owned transformer.
A utility padmount 500kVA transformer with has a 480V secondary feeding the main panel to building. The secondary rated current of this transformer is about 600A, however the buildings main panel and main breaker are rated 1200A. Although this 1200A is within the 250% rating of the secondary OCPD allowed by table 450.3(A) I dont know that this adequately protects the secondary of the transformer.
In the case of utility owened transformers is any consideration really given to protecting the secondary of the transformer since it is utility owned? Since it is a utility owned transformer does this even fall under the guidelines of the NEC?
Would you set the secondary OCPD to 600A to protect the transformer, or leave it at 1200A and let the utility worry about transformer protection?
A utility padmount 500kVA transformer with has a 480V secondary feeding the main panel to building. The secondary rated current of this transformer is about 600A, however the buildings main panel and main breaker are rated 1200A. Although this 1200A is within the 250% rating of the secondary OCPD allowed by table 450.3(A) I dont know that this adequately protects the secondary of the transformer.