secondary tap rules

Status
Not open for further replies.

shaw0486

Senior Member
Location
baltimore
I have a 45 KVA delta 480 wye 280 that sit inside and it feeds a piece of equipment outside about a hundred feet away. Doesnt the secondary need to be protected by a enclosed circuit breaker with in 25 feet and not a fused disconnect?
 
Last edited:
Unless dictated by some other reason, such as manufacturers requirements, any overcurrent device would suffice..fuse or breaker.
Being an outside tap, its possible none is needned {see 240.21(B)(5)}. Keep in mind, however, the requiremnts of Art 450 must also be met
 
I have a 45 KVA delta 480 wye 280 that sit inside and it feeds a piece of equipment outside about a hundred feet away. Doesnt the secondary need to be protected by a enclosed circuit breaker with in 25 feet and not a fused disconnect?

Technically the secondary of the transformer does not need protection.

The conductors on the secondary of the transformer do need protection per article 240.21(B).
 