What confuses me is the 125% rule when dealing with 600 volts or less. Is this combined or individually calculated. Thank you.
Ron,It would seem that 240.21(C)(1) indicates that a wye connected secondary cannot be protected by a primary only CB.
Then are can't add up the secondary CB's to be more than a single sized CB.
It depends on the facility. 240.21(C)(3)(2) allows you to 'combine' secondary devices, in an industrial facility. The other tap rules allow you to have multiple devices as long as you run directly from the transformer terminals to a single protective device.It would seem that 240.21(C)(1) indicates that a wye connected secondary cannot be protected by a primary only CB.
Then are can't add up the secondary CB's to be more than a single sized CB.
Don,
IMHO, 240.21(C)(1) indicates that the secondary conductors from a multiphase transformer cannot be soley protected by the primary of the transformer. So that means that secondary protection is required.
Jim,
I agree that note 2 allows multiple ocpd's but their summed total of the ratings cannot exceed that of a single device if it were provided.
Yes, that is correct, but I thought you were saying that 240.21 applies to the protection of the transformer secondary itself and not the secondary conductors.Don,
IMHO, 240.21(C)(1) indicates that the secondary conductors from a multiphase transformer cannot be soley protected by the primary of the transformer. So that means that secondary protection is required.
It is my opinion that all of the required protection for the transformer, both primary and secondary, is found in Article 450. The rules in 240 only apply to the protection of the conductors.450.3 is not about protecting the transformer secondary, it is about protecting the primary.
It is my opinion that the word "transformer" includes both the primary and secondary windings.450.3 Overcurrent Protection.
Overcurrent protection of transformers shall comply with 450.3(A), (B), or (C). As used in this section, the word transformer shall mean a transformer or polyphase bank of two or more single-phase transformers operating as a unit.
240.21 Location in Circuit.
Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply except as specified in 240.21(A) through (H). Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an overcurrent protective device meeting the requirements of 240.4.
It is my opinion that all of the required protection for the transformer, both primary and secondary, is found in Article 450. The rules in 240 only apply to the protection of the conductors.
It is my opinion that the word "transformer" includes both the primary and secondary windings.