Re: Section 110.14(A)
Bob (iwire) and Don.
One of the real disadvantages of my career is that, while I have a fair amount of installation experience, I have virtually no direct maintenance experience. I?ve certainly seen the results of poor maintenance and have been involved with a few product liability / system design (not mine
) lawsuits where both maintenance and initial installation were at issue. None of them had anything to do with torque though.
This is a typical excerpt from NFPA 70B:
Chapter 9 Motor Control Equipment:
9-3.2 Loose Connections.
Busbar and terminal connections should be inspected periodically to ensure that all joints are properly tightened. Proper torque is a function of bolt size, bolt type, terminal material, washer type, and type of busbar. Proper bolt torque values for all types of joints involved should be available in manufacturers? maintenance and instructional literature. It should not be assumed that busbar and terminal hardware, once tightened to proper torque values, remains tight indefinitely. (See Section 18-16, Infrared Inspection, which describes one method of detecting loose connections during the periods between shutdowns.)
I can?t do a ?cut and paste? of my NEMA documents but several of them are available as free downloads
here . Do a ?find? on ?maintenance,? and get a copy of PB.1 or 2 as an example. Other ?maintenance? documents are also available. They make similar statements; e.g., NEMA-PB.1 Section 10, Paragraph 10.4.2.
I don?t know which FM document is cited on Don?s referenced site. I do know both the NEMA and NFPA documents I mentioned are ANSI sanctioned, which technically makes them enforceable by FedOSHA?s ?general use? clause. I also know the FedOSHA enforceable FM standards are relatively limited ?product? standards listed
here.
All that being said, I think your experience is still valid. I have no unique knowledge of any torque requirements and manufacturer?s instructions vary. Some may say do nothing at all in absence of ?visual? evidence of over heating. NFPA 70B suggests infrared inspection. My point is you must know what a manufacturer?s torque instructions are to properly install/maintain equipment and it is as reasonable an addition to NEC mandatory text as 110.14(C)was.