As an electrical inspector, I see N.E.C. section 110.24 (Available Fault Current) not being addressed properly. Some electricians say "what is fault current" Others say I did not know that. I see arbritary numbers being place on service equipment. There was a large car dealership that went in in the city I inspect for. I was able to get the primary available fault current from the uitlity myself. I calculated the fault current my self based on the XFMR size and impedance, the calble length from the XFMR to the service equipment. The calculatioon that I came up with was not even close to the numbers the contractor had on the panel. Even figuring an infinite bus the numbers were not comparable. There was little motor contribution. So motor contribution was not a factor. In my opinion, I think a professional engineer should make the calculations. I submitted a public input for the 2017 (#3578) code cycle. My public input was not accepted. A professiona engineer submitted the same public input similar to mine and he received the same answer that I did. I just would like a general opinion on what other think. Please give me your opinion.
Herb