What section in the NEC permits sharing a neutral on 120V multi circuit outlets. or does each circuit need its own neutral wire?
For example..Ckt 1. 3. 5 have the same neutral?
Per section 210.4B they are telling me to us a simultaneous disconnect of all ungrounded conductors at the point where the branch circuit originates - i.e a 3-pole breaker would be required.
For example..Ckt 1. 3. 5 have the same neutral?
Per section 210.4B they are telling me to us a simultaneous disconnect of all ungrounded conductors at the point where the branch circuit originates - i.e a 3-pole breaker would be required.