NYC 2011
SECTION 210.52
Subsection 210.52(I) ? Add a new subsection 210.52(I) to read as follows:
(I) Outlet Requirements For Residential-Type Occupancies. In addition to the requirements set forth
in subsections (A) through (H) of this section, living rooms, bedrooms, dining rooms or similar rooms
shall have at least one receptacle outlet installed for air conditioners. Such outlets shall be supplied by an
individual branch circuit.
Exception: Buildings with central air conditioning systems that serve any of the above areas shall not
require separate outlets in those areas.