What does 422(presuming you meant).3 and 440.3 have to do with anything here?
210.8(F) requires GFCI protection (as was originally written whether that was a wise change or not) for all outdoor outlets at dwellings other than what was specifically mentioned. If you have a load to power you have an outlet associated with that load somewhere. There is nothing in either those articles that would eliminate needing to comply with anything in 210.8.
I do agree this probably was a bad move on the CMP. based on reports the AC units were the primary target that caused this change. Now with the TIA, they apparently realized at very least they jumped the gun on this.