piccard1898
Member
- Location
- Anaheim, CA
I interpret part 2 of 240.86(C) as:
the lower rated circuit breaker cannot have a load that exceeds 1% of that circuit breaker's AIC rating
(So I consider the "sum of the motor full-load currents" as a piece of equipment with multiple motors being fed with 1 circuit breaker).
Examples:
The system in these examples series rates to 65KAIC @ 277/480V (Available utility fault current is 30KAIC)
The downstream lower-rated circuit breaker is 14KAIC
Example1:
200A, 3P C/B in distribution section feeds panel A.
Panel A has:
(3) 80A, 3P circuit breakers that each feed a 30HP motor @ 40FLA = 120FLA
(1) 80A, 3P circuit breaker that feeds a piece of equipment with multiple motors for and 50FLA
So panel 'A' has a total motor load of 170FLA.
Example 2:
400A C/B in distribution section feeds panel B.
Panel 'B' has:
(1) 250A, 3P subfeed circuit breaker feeding a piece of equipment with multiple motors totaling @ 160FLA.
(For this example, the 250A subfeed circuit breaker is rated @ 14KAIC)
My interpretation of 240.86(C) is that example 1 is OK because each individual load on the downstream circuit breaker is less than 1% of its AIC rating.
Example 2 would violate the section because the load on the downstream circuit breaker exceeds the 1% of its AIC.
Can someone please clarify this for me.
If I am correct, how can I argue this to the planchecker????
Thank you.
the lower rated circuit breaker cannot have a load that exceeds 1% of that circuit breaker's AIC rating
(So I consider the "sum of the motor full-load currents" as a piece of equipment with multiple motors being fed with 1 circuit breaker).
Examples:
The system in these examples series rates to 65KAIC @ 277/480V (Available utility fault current is 30KAIC)
The downstream lower-rated circuit breaker is 14KAIC
Example1:
200A, 3P C/B in distribution section feeds panel A.
Panel A has:
(3) 80A, 3P circuit breakers that each feed a 30HP motor @ 40FLA = 120FLA
(1) 80A, 3P circuit breaker that feeds a piece of equipment with multiple motors for and 50FLA
So panel 'A' has a total motor load of 170FLA.
Example 2:
400A C/B in distribution section feeds panel B.
Panel 'B' has:
(1) 250A, 3P subfeed circuit breaker feeding a piece of equipment with multiple motors totaling @ 160FLA.
(For this example, the 250A subfeed circuit breaker is rated @ 14KAIC)
My interpretation of 240.86(C) is that example 1 is OK because each individual load on the downstream circuit breaker is less than 1% of its AIC rating.
Example 2 would violate the section because the load on the downstream circuit breaker exceeds the 1% of its AIC.
Can someone please clarify this for me.
If I am correct, how can I argue this to the planchecker????
Thank you.