electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
I agree if you were to have a length rule, then it should be clarified that they can be spliced and don't have to be continuous to that length
So you're for deleting the 6" rule altogether? So 2" of wire in the box is acceptable?But if the rule is just deleted, then wouldn't there be nothing prohibiting splicing/extending them?
YesSo you're for deleting the 6" rule altogether? So 2" of wire in the box is acceptable?
But then invariably there would be guys leaving 2" in the box. Like I said previously if inspectors used some common sense the new wording wouldn’t be needed. This reminds me of the 2008 NEC where they had to add wording stating that the common mounting holes in metal boxes aren't required to be sealed becuse inspectors where having guys seal them as unused openings.But if the rule is just deleted, then wouldn't there be nothing prohibiting splicing/extending them?
Respectfully, if the gentleman in the video, after texting, still needed to call Paul and further discuss the matter for half an hour before coming to an agreement, and then needed to reach out to the NFPA for validation, it seems to me that it might not be as cut and dry as that. Until the code is clarified that each individual conductor must be separately extended I believe that people will continue to interpret it both ways.I agree this may add additional wire nuts in the box but I don't see this as being open to interpretation. All it says is that each conductor must meet the minimum length requirement. If one or more do not then they can be individually extended via a splice to meet the minimum length. Since wire nuts do not count towards box fill they don't change anything regarding the number of conductors permitted within the box.
From Mike Holt:
I always leave at least that much. If you properly plan out your cable runs and use large boxes folding the conductors in is never an issue.Dennis, you left 6" past the front of the box."
Why would they do that? I guess if they want to put in a device with 2 in sticking out, let them have at it. Someone wanting more length can add tails.But then invariably there would be guys leaving 2" in the box.
In my area it's because "I said so" or they aren't listed for grounding.Also, I never understood the advantage of using "greeners".
If your going to use a wirenut on the EGC why not use the same type you're already using for the other conductors?
Oh well,,
Jap>
Really, someone actually says that a wirenut need to be listed for grounding? Greenies are only listed for EGC's. That doesn't mean that a standard wirenut cannot be used. Where do they find these guys.In my area it's because "I said so" or they aren't listed for grounding.
I always thought that the main advantage is a quicker install just cut one of the romexes slightly longer on rough in.
In my area it's because "I said so" or they aren't listed for grounding.
Regular Ole wirenuts. For the record there is no requirements for a wirenut to be so listed.What aren't listed for grounding?
Jap>
Regular Ole wirenuts. For the record there is no requirements for a wirenut to be so listed.
What about 250.8 (a) 8?Regular Ole wirenuts. For the record there is no requirements for a wirenut to be so listed.
Regular ole wirenuts are already covered under 250.8(A)(1).What about 250.8 (a) 8?
Devil's advocate here.