Securing and Supporting NEC 330.30 (B)

Status
Not open for further replies.

Jamar

Member
Location
Alaska
500 kcmil MC-HL first support outside of a panel box or penetration.

a) 12"

b) 3 ft.

c) 6ft.

Please explain your answer.

NEC Code only


It's an argument I have on every new job. Not only with other journeyman bit with QC's and QA's.

Sent from my SM-G935T using Tapatalk
 

Smart $

Esteemed Member
Location
Ohio
ANSWER: c) 6 ft.

330.30(B), first sentence permits up to 6 ft intervals. Second sentence does not apply for larger than 10 AWG. Third sentence as of 2014 edition, 250kcmil and larger installed vertically the distance can be up to 10 ft.
 

Jamar

Member
Location
Alaska
ANSWER: c) 6 ft.

330.30(B), first sentence permits up to 6 ft intervals. Second sentence does not apply for larger than 10 AWG. Third sentence as of 2014 edition, 250kcmil and larger installed vertically the distance can be up to 10 ft.
Exactly. Thanks