Re: Selecting ambient temperature correction factors from Ta
Please note that ?sentence 1? also does not tell us how to select the ampacity of the conductor. That we get from Table 310.16. It is that Table that tells us to adjust for ambient temperatures in excess of 30C.
So I did not completely address your earlier question:
Going back to Bob's initial statement, this section is in need of clarification.
I would prefer to say that ?sentence 1? does not address temperature correction factors at all. It doesn?t tell us they apply, and it doesn?t tell us they don?t apply. It just talks about using the (termination?s) 75C rating, when selecting the ampacity of the conductor.Originally posted by lauraj: Sentence 1 still seems to me that it is just dealing with conductor ampacity and terminal ratings if there are no correction factors applied.
Please note that ?sentence 1? also does not tell us how to select the ampacity of the conductor. That we get from Table 310.16. It is that Table that tells us to adjust for ambient temperatures in excess of 30C.
So I did not completely address your earlier question:
I should have said ?110.14(C), sentence 1, in conjunction with the Table 310.16 Correction Factors.? By that, I mean that you can't complete the actions described in 110.14(C), sentence 1, without also going to Table 310.16 to find the ampacity values.Where in the code does it say that I need to use the temperature adjustment factor based off the rating of the terminal and not the conductor?
Going back to Bob's initial statement, this section is in need of clarification.