I wanted to hear the philosopy of others when it comes to selecting the size of a tie-breaker in LV equipment (Switchgear, MCC', etc..)
I have heard some arguments that you don't need to size the tie for the same size as the mains or bus since the ties will only see half of the total load on the equipment when its being operated through the tie. So for instance on Switchgear that has an 1600A Mains and Bus you might only find an 800A tie breaker.
I have heard others say that sizing the Tie breaker the same as the mains and bus is a good idea because it provides spare breakers that are sized the same as the mains if you ever needed to replace mains for some reason. Plus I heard that the incremental cost for a tie breaker sized the same as the mains is not that much more than if it is sized at at only half of the mains and therefore may make economical sense.
Was curious to hear the opinions and experiences of others.