thebozak
- Jersey City, NJ, USA
First time posting to the forum, long time reader.
This is an NEC based question. Our typical design for a chemical plant install is Class I Div 2 area is with a type z purge/press control panel located in the hazardous area, non-incendive instrumentation, and insulated conductors in rigid galvanized steel conduit to connect. The only seals we install typically are at the control panel (to block purge flow, not necessarily to provide explosionproof protection) or at powered instrumentation when required. Voltages are typically 24VDC or 120AC for the power instruments.
At the bottom of all enclosures and vertical conduit runs, we typically install a Crouse-Hinds ECD18 "combination" breather/drain which is rated Class I Div 2 Group C,D. Are we overspecifying? Could this be an ordinary location breather drain?
If required to be hazardous rated per the area, can anyone suggest a suitable replacement (preferably a combination type) that would also cover Group B or CD + H2?
Thanks.
Thanks.
