700.27: Emergency system(s) overcurrent devices shall be selectively coordinated with all supply side overcurrent protective devices. (The handbook says this is new for 2005.)
Is it just me, or is this impossible? How does one acheive this? I've been comparing some circuit breaker curves with SKM software, and above a certain current, it seems to be anyone's guess which breaker will trip first.
For example, the following curves show a standard Square D 20A QO breaker, a 100A LE breaker, and a 800A GE TKMA breaker. (Imagine a 800A main in a switchboard, feeding a 100A panel with some 20A branch circuits.)
It looks to me like above about 800A, the 100A feeder breaker may trip instead of the 20A branch breaker. And above about 2000A, the 800A breaker may trip before the 20A. Is that right? Does "selective coordination" also include the instantaneous region also?
So what does one do? Do I have to replace all the NQOD branch panels (that fit nicely inside a wall) with a room full of fusible switches?