I just finished a Selective Coordination and Arcflash study.
Power runs to the site some 5 miles from the substation on overhead poles through 2/0 Okonite conductors. At the site there is a 225 KVA transformer with 25 A 12470 V Bay O Net fuses on the PRIMARY.
Both my Selective Coordination and Arcflash calculations change when I include these PRIMARY fuses in my study.
Without the primary side Bay O Net fuses in the study the site has high Arcflash levels and poor coordination. With the primary side Bay O Net fuses in the study , the site has acceptable Arcflash levels and acceptable coordination.
Should I include these Fuses in my Selective Coordination and Arcflash study?
Power runs to the site some 5 miles from the substation on overhead poles through 2/0 Okonite conductors. At the site there is a 225 KVA transformer with 25 A 12470 V Bay O Net fuses on the PRIMARY.
Both my Selective Coordination and Arcflash calculations change when I include these PRIMARY fuses in my study.
Without the primary side Bay O Net fuses in the study the site has high Arcflash levels and poor coordination. With the primary side Bay O Net fuses in the study , the site has acceptable Arcflash levels and acceptable coordination.
Should I include these Fuses in my Selective Coordination and Arcflash study?