Panel Statement: The ?Accept in Principle? wording accepted by CMP 10 during ROP meeting, clearly does not contain a requirement for when or where selective coordination is required. It does however clarify the definition of ?Coordination, Selective?. This clarification is necessary because, as described in the original substantiation;
The NEC needs to remain the quintessential document for the electrical system safety issue, and while the existing definition has served us well for many years, it is now necessary to clarify the definition, not change the meaning. The proposed changes add the specific clarity that is needed.
The wording accepted by CMP 10 is necessary to distinguish between the word ?Coordination? and the phrase ?Selective Coordination?. The word ?Coordination? is often used to describe the isolation of downstream overcurrent conditions over limited ranges of time and currents, but selective coordination is used to describe the isolation of downstream overcurrent conditions over the complete range of available overcurrents and the times associated with those overcurrents.
The 0.1 second limit for isolation of downstream overcurrent conditions, referred to in the substantiation of the submitter in the reference to NFPA 99, actually describes ?Coordination? down to 0.1 seconds, not ?Selective Coordination? down to 0.1 seconds.
?Total Coordination? is synonymous with the phrase ?Selective Coordination?. The words ?coordinate? or ?coordination? alone are simply not sufficiently specific enough to describe the concept as utilized by CMPs 12, 13, and 20.