BL-170 feeds panelboard with branch breaker BL-171. BL-171 is in series with downstream breaker BL-172
These are emergency loads.
Question:
Does BL-172 need to coordinate with BL-170?
My opinion is no, because BL-171 will trip before BL-170.
But my coworker has a different opinion. He says yes, because the code states:
His argument is that all supply-side, means BL-170 is a supply-side device relative to BL-172.
What do you think?
These are emergency loads.
Question:
Does BL-172 need to coordinate with BL-170?
My opinion is no, because BL-171 will trip before BL-170.
But my coworker has a different opinion. He says yes, because the code states:
700.27 Coordination. Emergency system(s) overcurrent devices shall be selectively coordinated with all supply-side overcurrent protective devices.
His argument is that all supply-side, means BL-170 is a supply-side device relative to BL-172.
What do you think?