mshields
- Boston, MA
I am specifying a 100kW, 208Y/120V diesel standby generator to serve a classroom building at a local University. I am working with the Eaton breaker combinations to achieve0.01 selectivity on the Emergency Branch. Here I should tell you that I plan to have a 300A optional standby ATS and a 150A, Article 700, Emergency branch.
The key to finding breakers that will work in series, from the 450A main to the 150A Emergency branch and lastly to the 20A-1P breakers mostly for emergency lighting, is low fault current. If the fault current is low enough, one can find the breakers using the manufacturer's selectivity combination tables (or via plugging into SKM - it matters not). But here's where I'm running into a problem. Caterpillar is telling me that the reactances on these relatively small generators is no higher than 8%. I need higher than that to make this work.
Does that 8% number sound right to you? I have always thought generators were more typically in the 16% range.
Any suggestions would be appreciated.
thanks,
Mike
thanks,