The whole reason for self grounding devices when mounting in a flush type box is to make sure the grounding path is not broken, a surface mounted box will have yoke to box contact when one of the retainer washers is removed, but this can not be guaranteed on a flush mounted box, as far as the UL listing being violated if longer screws are used? well I think you would have another violation if your needing longer screws like 314.20 (2002)
And as far as I can remember the screws that connects a mud ring to the 1900 box is listed for bonding between the mud ring and box, we went through this a while back with a couple of our inspectors saying we had to bond around every mud ring, but they lost that one.